Thread: Over sizing the breaker question?

Hybrid View

DiabolicZ Over sizing the breaker... 03-23-2011, 07:14 AM
kenwhite As long as the cable... 03-23-2011, 10:47 AM
A/C Guy There are 2 ways that people... 03-23-2011, 02:55 PM
kenwhite This really should never be... 03-23-2011, 03:25 PM
A/C Guy There is no such requirement... 03-23-2011, 03:54 PM
kenwhite Like I said, every branch... 03-23-2011, 04:56 PM
ASE_MasterTech Sorry, but this statement... 03-24-2011, 12:22 AM
performance There is a section in the NEC... 03-24-2011, 02:08 AM
ASE_MasterTech I beg to differ, but 'normal... 03-24-2011, 03:40 AM
DiabolicZ I could see that happening.... 03-24-2011, 04:42 AM
kenwhite Duty cycle is an important... 03-24-2011, 10:46 AM
ASE_MasterTech Ok then, let me put this... 03-24-2011, 10:02 PM
performance There isn't a certificate of... 03-24-2011, 10:29 PM
kenwhite The thing you have to... 03-24-2011, 10:48 PM
kenwhite Oh, and one other thing. ... 03-24-2011, 10:59 PM
ASE_MasterTech OK, I'll rephrase.. Here in... 03-25-2011, 10:16 PM
A/C Guy If a branch has multiple... 03-27-2011, 02:34 AM
kenwhite Well, there are mimimum... 03-27-2011, 12:09 PM
Canada I can think of only one... 04-09-2011, 05:34 PM
ASE_MasterTech There's not always time to... 04-09-2011, 05:54 PM
ASE_MasterTech This may have been the case... 03-26-2011, 12:01 AM
dgarnier lucky you only had to get... 03-27-2011, 12:12 PM
geezer There are 3 things that... 03-27-2011, 04:48 AM
kenwhite Geezer you must derate the... 03-27-2011, 12:25 PM
kenwhite There seems to be some... 03-27-2011, 01:44 PM
geezer Interestings facts to be sure... 03-27-2011, 03:54 PM
kenwhite Well, the ampacity for a... 03-27-2011, 04:08 PM
Canada That was the point. How many... 04-16-2011, 11:46 PM
Previous Post Previous Post   Next Post Next Post
  1. #1

    Default

    There isn't a certificate of occupancy permit for private residences after a structure is built in many states...At least not in this one. IF the correct plug is used, then it will be obvious, since the 6-50 is the only standard plug for single phase 220V welders and cutting equipment. The camper won't plug in.

  2. #2

    Default

    The thing you have to consider when looking at the duty cycle, is that while the continuous current limit may be exceeded for short periods of time, the average current based on the duty cycle load is typically much less than rated continuous current.

    If the branch has multiple loads, the breaker would still trip trip if severly overloaded when multiple loads are being used - normally a thermal breaker is specified for this type of circuit.

    Article 630 is really written for commercial/light industrial use with exceptions for residential/home use of a welder.
    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

  3. #3

    Default

    Oh, and one other thing.

    Just because a certain welder draws X# of amps, this does not mean that a certain AWG wire needs to be installed.

    There are many factors that I listed in post #6 above that actually determine the size and type of cable that must be used.

    Insulation type is also very, very, important when determining where the run can be placed and how much of the cable's ampacity will have to be derated...

    EDIT: As Mark stated in his first post, if your are not comfortable doing all or part of the wiring upgrade, hire a competent electrician to either do it for you, or help you do it...
    Last edited by kenwhite; 03-25-2011 at 01:34 PM. Reason: Add Info... change referenced post
    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

  4. #4

    Default

    OK, I'll rephrase..
    Here in the northeast most states I know require a 'Certificate of Occupancy' (& the accompanying inspections) be issued for any incoming occupant, be it renters-leasers-owners, commercial or residential. Structures/buildings are required to meet or exceed the code requirements in force at time of construction or most recent renovation, excluding 'fire code' issues which must be up to date.
    Here in NJ, after owning 4 homes, 2 Amoco Service Stations, & currently working for Government, I can tell you that 6awg has been required on any 50amp outlet circuit I installed or had installed. This is 'code' here regardless of NEC recommendations, & IMHO just good common sense for wire buried in a wall or conduit whose future use may or may not involve a 'protected' or 'limited duty' device..
    -at the job-
    Miller Dynasty 200DX
    Miller Syncrowave 350
    MillerMatic 250 (several)
    Millermatic 350
    Miller Bobcat 250 (Service Truck)
    Lincoln AC225 (many)
    Miller Spectrum 625 Plasma (several)
    -At Home-
    Everlast PP256
    Longevity 256PI
    "Slow is smooth, smooth is fast.."

  5. #5
    Join Date
    Mar 2011
    Location
    Apache Junction, Az
    Posts
    90

    Default

    Quote Originally Posted by kenwhite View Post
    The thing you have to consider when looking at the duty cycle, is that while the continuous current limit may be exceeded for short periods of time, the average current based on the duty cycle load is typically much less than rated continuous current.

    If the branch has multiple loads, the breaker would still trip trip if severly overloaded when multiple loads are being used - normally a thermal breaker is specified for this type of circuit.

    Article 630 is really written for commercial/light industrial use with exceptions for residential/home use of a welder.
    If a branch has multiple loads, the breaker size should equal the sum of the loads with the appropriate wire used. If the breaker is tripping as in your statement, then the wrong supply wire and breaker was installed. We install multiple appliances on a single circuit regularly for commercial buildings. We use a larger supply wire on that circuit and the larger breaker equal to the sums of the maximum of the appliances and each appliance has it's own individual fused disconnect with the appropriate size fuses for that one appliance.
    Hobart Handler 175
    Hobart Iron Man 230 with spool gun
    Thermal Dynamics Cutmaster 52
    Makita Cold Cut Saw

    Possible future addition:
    Lincoln Invertec V311
    or Miller Dynasty 350
    or ???

  6. #6

    Default

    Quote Originally Posted by A/C Guy View Post
    If a branch has multiple loads, the breaker size should equal the sum of the loads with the appropriate wire used. If the breaker is tripping as in your statement, then the wrong supply wire and breaker was installed. We install multiple appliances on a single circuit regularly for commercial buildings. We use a larger supply wire on that circuit and the larger breaker equal to the sums of the maximum of the appliances and each appliance has it's own individual fused disconnect with the appropriate size fuses for that one appliance.

    Well, there are mimimum requirements for branch circuit design as well as load duty cycle, demand factor, requirements.

    I never said the breaker would trip excessively, I said it would still protect the branch correctly even when overloaded with many circuits on the branch energized at once.

    The rest of your post reinforces my previous points...

    Last edited by kenwhite; 03-27-2011 at 01:57 PM.
    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

  7. #7
    Join Date
    Apr 2011
    Location
    Sasktachewan, Canada
    Posts
    95

    Default

    I can think of only one anwser to this post:

    "There is never time to do it right but there is always time to do it over!"
    Attitude Determines Altitude

  8. #8

    Default

    Quote Originally Posted by Canada View Post
    I can think of only one anwser to this post:

    "There is never time to do it right but there is always time to do it over!"
    There's not always time to 'do it over', particularly when your house/shop is a pile of ash.
    just a thought...
    -at the job-
    Miller Dynasty 200DX
    Miller Syncrowave 350
    MillerMatic 250 (several)
    Millermatic 350
    Miller Bobcat 250 (Service Truck)
    Lincoln AC225 (many)
    Miller Spectrum 625 Plasma (several)
    -At Home-
    Everlast PP256
    Longevity 256PI
    "Slow is smooth, smooth is fast.."

  9. #9

    Default

    Quote Originally Posted by performance View Post
    IF the correct plug is used, then it will be obvious, since the 6-50 is the only standard plug for single phase 220V welders and cutting equipment. The camper won't plug in.
    This may have been the case previously, but a 'standard' is not a rule, & with the emergence of multi-voltage welders/cutters this 'standard' is disappearing.
    The Miller Dynasty 200DX's we have on the job are voltage sensing from 110v to 220v & as so are equipped with a neutral (4 wires out of the machine). We wire the machine with a 30amp 4 pronged plug & then run adapters for the 220v-30amp/110v-20amp outlets we may encounter when moving from area to area.
    -at the job-
    Miller Dynasty 200DX
    Miller Syncrowave 350
    MillerMatic 250 (several)
    Millermatic 350
    Miller Bobcat 250 (Service Truck)
    Lincoln AC225 (many)
    Miller Spectrum 625 Plasma (several)
    -At Home-
    Everlast PP256
    Longevity 256PI
    "Slow is smooth, smooth is fast.."

Similar Threads

  1. Breaker size for 255EXT?
    By Seshan in forum General Welder Questions
    Replies: 16
    Last Post: 07-20-2014, 01:10 PM
  2. Looking for Special 12 VDC Circuit Breaker
    By cbmkr in forum Tips & Tricks, Custom Tools, Safety, Ideas and Reviews.
    Replies: 11
    Last Post: 12-03-2012, 12:43 PM
  3. Sizing the neutral
    By posixPilot in forum General Welder Questions
    Replies: 12
    Last Post: 01-28-2012, 03:52 PM
  4. 30 amp breaker for PM205
    By www in forum Multi-Process Units (TIG,Stick,Plasma/MIG,TIG,Stick Combo units)
    Replies: 12
    Last Post: 04-27-2010, 04:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •