Originally Posted by
kenwhite
Like I said, every branch that has a socket has its breaker sized for the cable insulation type, cable run length, # of cables bundle togther, load duty cycle, and cable AWG size to protect the wiring. It is the manufacturers responsibility to fuse/breaker if they want to protect the end user equipment from excessive damage or fire hazards.
The breaker protects the wiring between the socket(s) and panel, it is not sized or designed to protect the equipment that is plugged into the socket.
Oh, and my furnace is hard wired into a fused disconnect and not plugged into a 120 V wall socket - this is per the manufacturers recommendation, so be careful when you use the word every...
Typically the minumum fuse/breaker size is recommended for proper operation so the circuit is not being interrupted often when trying to use the device.
I have installed every brand of furnace sold in the US. Not one requires hard wiring and a fused disconnect per the manufacturer. If your furnace is installed that way it is because of local codes.
Very few manufacturers list a minimum fuse. Most only list a maximum fuse or breaker size.