    Quote Originally Posted by A/C Guy View Post
    There is no such requirement or legal implication of responsibility. For example, every furnace in the US is installed with a plug in cord. No furnace in the US has any built in breaker or fused protection. Same can be said for table saws, chop saws, corded drills, vacuum pumps, etc. Every welder does state a max fuse or breaker for the device. That transfers all responsibility to the operator.
    Like I said, every branch that has a socket has its breaker sized for the cable insulation type, cable run length, # of cables bundle togther, load duty cycle, and cable AWG size to protect the wiring. It is the manufacturers responsibility to fuse/breaker if they want to protect the end user equipment from excessive damage or fire hazards.

    The breaker protects the wiring between the socket(s) and panel, it is not sized or designed to protect the equipment that is plugged into the socket.

    Oh, and my furnace is hard wired into a fused disconnect and not plugged into a 120 V wall socket - this is per the manufacturers recommendation, so be careful when you use the word every...

    Typically the minumum fuse/breaker size is recommended for proper operation so the circuit is not being interrupted often when trying to use the device.

    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

  2. #2
    Join Date
    Mar 2011
    Location
    Apache Junction, Az
    Posts
    90

    Default

    Quote Originally Posted by kenwhite View Post
    Like I said, every branch that has a socket has its breaker sized for the cable insulation type, cable run length, # of cables bundle togther, load duty cycle, and cable AWG size to protect the wiring. It is the manufacturers responsibility to fuse/breaker if they want to protect the end user equipment from excessive damage or fire hazards.

    The breaker protects the wiring between the socket(s) and panel, it is not sized or designed to protect the equipment that is plugged into the socket.

    Oh, and my furnace is hard wired into a fused disconnect and not plugged into a 120 V wall socket - this is per the manufacturers recommendation, so be careful when you use the word every...

    Typically the minumum fuse/breaker size is recommended for proper operation so the circuit is not being interrupted often when trying to use the device.
    I have installed every brand of furnace sold in the US. Not one requires hard wiring and a fused disconnect per the manufacturer. If your furnace is installed that way it is because of local codes.
    Very few manufacturers list a minimum fuse. Most only list a maximum fuse or breaker size.
    Hobart Handler 175
    Hobart Iron Man 230 with spool gun
    Thermal Dynamics Cutmaster 52
    Makita Cold Cut Saw

    Possible future addition:
    Lincoln Invertec V311
    or Miller Dynasty 350
    or ???

  3. #3

    Default

    Quote Originally Posted by A/C Guy View Post
    I have installed every brand of furnace sold in the US. Not one requires hard wiring and a fused disconnect per the manufacturer. If your furnace is installed that way it is because of local codes.
    Very few manufacturers list a minimum fuse. Most only list a maximum fuse or breaker size.
    That is funny because every HVAC forced hot air system I have seen is hardwired, and I did a quick search and found a few product manuals that require it too. In these manuals the manufacturer typically lists what type of safety disconnect and fuse/breaker is suggested too.

    I have never seen a maximum fuse size listed for a plug in device, only a mimimum size for proper operation to avoid excessive tripping.

    For hard wired devices, the recommended cable size, breaker/fuse, and disconnect is listed with the caveat that each installation is different and subject to local codes.
    Last edited by kenwhite; 03-27-2011 at 02:01 PM.
    __________________________
    Everlast Power I-MIG 200
    Everlast PowerUltra 205P
    Everlast SM 200-N
    Thermal Dynamics Cutmaster 42

Similar Threads

  1. Breaker size for 255EXT?
    By Seshan in forum General Welder Questions
    Replies: 16
    Last Post: 07-20-2014, 01:10 PM
  2. Looking for Special 12 VDC Circuit Breaker
    By cbmkr in forum Tips & Tricks, Custom Tools, Safety, Ideas and Reviews.
    Replies: 11
    Last Post: 12-03-2012, 12:43 PM
  3. Sizing the neutral
    By posixPilot in forum General Welder Questions
    Replies: 12
    Last Post: 01-28-2012, 03:52 PM
  4. 30 amp breaker for PM205
    By www in forum Multi-Process Units (TIG,Stick,Plasma/MIG,TIG,Stick Combo units)
    Replies: 12
    Last Post: 04-27-2010, 04:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •