Originally Posted by
everlastsupport
If L1 is 120vac to ground and L2 is 120vac to ground, they are 120 degree out of phase, not 180 degrees like standard single phase power.
Not sure what the power supply will think about that.
Maybe you can rent a good (AVR or diesel) generator, or this can be a good excuse to buy one.
Did you look for 110vac outlets in the place like we talked about and tried to trace them to a panel with 220? In commercial buildings, I see 220vac 1PH separate from the 208, 277, 480 all the time.