    You'll need a 30 amp breaker.

  2. #2

    Default

    Maybe my hobart transformer doesn't put out the amperage it claims. performance, in the above post is an Everlast tech while I'm just a hobby welder so always take the Everlast company advice over mine.
    2013 250EX : SSC Pedal : I-MIG 250P 20' Profax gun : Power Plasma 60 p80 torch : 3M Speedglas 9100XX : Evolution Rage 3 DB cold saw

  3. Default

    Quote Originally Posted by performance View Post
    You'll need a 30 amp breaker.
    This may be a question for my electrician but if it is a 20 amp breaker can I just switch the breaker out for a 30 amp? Or would that be pointless because the wire gauge going to the outlet is most likely for a 20 amp?

  4. #4
    Join Date
    May 2012
    Location
    Disneyland
    Posts
    2,662

    Default

    Quote Originally Posted by esg612 View Post
    This may be a question for my electrician but if it is a 20 amp breaker can I just switch the breaker out for a 30 amp? Or would that be pointless because the wire gauge going to the outlet is most likely for a 20 amp?
    NO! do not just swap the breaker. As you said the wiring will be only rated to 20 amps. The breaker is to protect the wiring, not the load.

    You can go ahead and use that 20 amp circuit for welding at most power levels. You may trip the breaker on extended welds at max power, but you might not. Just try it and see before you decide to add a new circuit. A lot depends on the length of wiring and the voltage at the panel, and any other loads on that circuit. Try to have the welder be the only thing on that breaker when welding. Also keep in mind the duty cycle of your welder. You don't want to exceed that. 3.5 minutes welding, 6.5 minutes cool down at max power.
    Long arc, short arc, heliarc and in-the-dark!

  5. #5

    Default

    If the outlet and circuit is only used for running the unit, it shouldn't hurt. In fact when running the unit only pulls about 20 amps, but the inrush is higher, so you have to have a larger breaker. Now with that said, the wire requirements ARE reduced per the NEC according to section 630.

Similar Threads

  1. New guy with 250ex questions.
    By gree box in forum TIG Welding (GTAW/GTAW-P)
    Replies: 26
    Last Post: 01-29-2013, 10:11 PM
  2. 256 questions
    By tnc110 in forum Multi-Process Units (TIG,Stick,Plasma/MIG,TIG,Stick Combo units)
    Replies: 43
    Last Post: 05-02-2012, 01:03 PM
  3. Pu 205 questions please
    By Dne007 in forum Multi-Process Units (TIG,Stick,Plasma/MIG,TIG,Stick Combo units)
    Replies: 4
    Last Post: 03-13-2012, 08:12 PM
  4. spool gun questions
    By Ram48 in forum MIG Welding (GMAW/GMAW-P/FCAW)
    Replies: 2
    Last Post: 10-25-2011, 01:34 AM
  5. 250EXT Questions
    By zoama in forum TIG Welding (GTAW/GTAW-P)
    Replies: 2
    Last Post: 09-08-2011, 01:20 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •