Originally Posted by
RichardH
Does the picture here include a GFCI on either the grinder's or the welder's outlet? I would have expected them to trip. (I know GFCI detects an imbalance between hot-hot or hot-neutral currents; do they also trip if current is detected on ground?)
Considering how the current smoked the 120v receptacle, it'd be wise to inspect the ground wiring from the 120v receptacle back to the panel's bus, and do the same for the 240v circuit, particularly the ground wires inside the welder.
I'm trying to grasp why the electrical path would prefer the building ground over the heavy ground clamp wire. It'd guess it's because the short was actually on the torch lead, so a path existed from the ground clamp, to the building ground via the grinder, through the case, and to the torch lead. This would have been a much lower resistance path than through a spark gap to the torch electrode, which would explain why it wouldn't strike an arc, yet current was flowing through the grinder as soon as you hit the pedal.