Just wondering what breaker size I need for the 255EXT, The site says max inrush @ 220v is 33.6A, So should I get a 40A breaker?
Thanks :)
Printable View
Just wondering what breaker size I need for the 255EXT, The site says max inrush @ 220v is 33.6A, So should I get a 40A breaker?
Thanks :)
lcome, Seshan! Are you getting a 255?!
Yes, the breaker is there to protect the wire ,not the machine. So do not use a bigger breaker than what the wire is rated for. I have my welder outlets wired for 50 amps and breakers to match. That way I can plug any single phase welder and plasma in that I have. there is no problem plugging in a machine that only draws 35 amps into a 50 amp circuit. I think the 255 comes with a 50 amp cord end on it or no plug at all and the purchaser needs to buy a plug.
If it's not a lot more money, I would go with a 50 amp. Like Gary said it is there to protect the wire, the unit will protect itself. But a 50 amp will allow bigger machines down the road if needed.
I don't think I will need bigger machine anytime soon, and when I do I'll probably be living somewhere else (aka not my parents house :P ).
I was also thinking that since we (north america) are actually on 240v that the machine would draw less amps, about 3.05A less, (if I did my math right), so about 30A inrush.
50A would be standard for any welder circuit and allow additional products to be used on the circuit that might require mor such as Mike said, a plasma.
If its anything like US actual voltage is more like 230-235v. Not all 8ga copper wire is equal it seems. I've seen some rated at 40 amps and some 55 amps.
There is a thread where I asked all the same questions with a lot of good explainations for wire size and breakers. Just search for my posts. The guys helped me a lot.
It's not up to the wire, it's the NEC that sets how much current is allowed for what size wire runs. There are different rating for different temperature insulation ratings, along with raceway type and distance calculations. You local codes will also supersede the NEC for some things.
Ah yes. Here's the simplified, (meaning other factors are ignored) relevant chart.
http://www.usawire-cable.com/pdfs/NEC%20AMPACITIES.pdf
Thanks for pointing that out.
rivets