What would the recommended type and ga. wire for a 60ft run be?
Machine is a 250EX.
220v 3 wire hookup.
Printable View
What would the recommended type and ga. wire for a 60ft run be?
Machine is a 250EX.
220v 3 wire hookup.
No 8 should do the trick, with a 50 amp breaker, you can verify this by using one of the many wire size calculators available on the web.
Thank you. I picked up the #8 wire, 50Abreaker, plug, receptacle and Argon bottle today. I should have it wired this weekend and the water cooler should be here Monday.
A 40 amp breaker would not work at my shop on the 250EX as I was getting 208 volts off the 3phase supply and the inrush would pop the breaker, so I had to run over reset the breaker and run back and turn on the 250Ex again so it would run before the capacitators bleed down,,,,worked fine once I got it started,,,,took me a while to figure out that 208 volts requires a larger breaker on the supply side for the in rush demand of the machine...if I had 220 or 240 volts a 40 amp breaker would be fine...